Hi all

I have a project that uses a Siemens 315-2DP and two HMI's.

The two HMI's are at separate ends of the line. One of the HMI's has a product recipe list on it and I'd like to display the same recipe on the other HMI.

They are linked via profibus.

I wondered if there is any way of displaying/editing the first HMI's product recipe list on the 2nd HMI ??

I've tried setting up a recipe in WinCC Flex but I'm not sure how I'd link it to a recipe on another screen??

I'm new to WinCC Flex and wondered if anyone out there has any ideas, or knows whether this is even possible?

Many thanks for any light you can shed on this..

(y)
 
I think you could program it but it would not be easy. I would look into the Smart Access option on the panels. You could then see the first panel on the second and have full control of it from the second panel.
 
uptown47,

I have run into a similar problem on several projects so far. The only solution I have found is to link the 2 HMI's with ethernet and use smart server / smart access.

Hope this helps
 
Thanks for your answers Charles and nhart,

I've been looking into it this afternoon and I've drawn the same unfortunate conclusion myself...

I'm trying something else now which will hopefully negate the need for me to have the recipes on both screens.

Many thanks

:)
 
Maybe you can upload 1 recipe to the cpu and download it from there too the second HMI using the 'mailbox'.
 

Similar Topics

In the past when testing a particular HMI with a CLX program I'd use rsemulate with rslinx virtual backplane driver and create a dde topic for the...
Replies
3
Views
2,155
I have ML1500 and PV1000+. I would like to display the parameter value in the ML1500 on the PV1000+. The following configuration is impossible or...
Replies
6
Views
3,921
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
Replies
4
Views
218
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
346
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
1
Views
178
Back
Top Bottom