shiftedbits
Member
Having a brain freeze.
I am trying to figure out how to calculate an underrange RAW value for a PLC-5 1771 analog input card set for 4-20ma input range with 0(Raw Min) To 4095(Raw Max).
Instrument Range = 4 ~ 20ma (50 to 100degF)
Suppose the instrument fails and It's now outputting a 3.0ma signal instead of 4.0ma which is the low scale value. How do I calculate the PLC raw data value for this?
3.0ma is going to be a negative value since instrument 0 = PLC Raw count of zero.
Without changing the analog card set-up
Q1. Can AB's analog data reigster for a channel have a negative number (instead of 0 to 4095) if it's raw count is set as 0 To 4095 and is set-up for a 4-20ma signal?
Q2. I don't want to use the under-range bit for this but instead of looking for the actual raw value at 3.0ma. Can this be done? If it can, How would I find (formula) the actual negative value at 3.0ma?
Thanks all!
I am trying to figure out how to calculate an underrange RAW value for a PLC-5 1771 analog input card set for 4-20ma input range with 0(Raw Min) To 4095(Raw Max).
Instrument Range = 4 ~ 20ma (50 to 100degF)
Suppose the instrument fails and It's now outputting a 3.0ma signal instead of 4.0ma which is the low scale value. How do I calculate the PLC raw data value for this?
3.0ma is going to be a negative value since instrument 0 = PLC Raw count of zero.
Without changing the analog card set-up
Q1. Can AB's analog data reigster for a channel have a negative number (instead of 0 to 4095) if it's raw count is set as 0 To 4095 and is set-up for a 4-20ma signal?
Q2. I don't want to use the under-range bit for this but instead of looking for the actual raw value at 3.0ma. Can this be done? If it can, How would I find (formula) the actual negative value at 3.0ma?
Thanks all!