295
HI
What cable and procedure do I need according to upload / download the panelview file . THe plc is micrologix 1500 and panelview 300 has DF1 port Thanks
 
Last edited:
The cable needed from your PC/laptop to the PV is a 9 to 9 pin straight thru cable.
The cable needed from your ML1500 ( 8 pin port) to your PV is AB's 2711-NC21 or 22 ( its also a straight thru cable ( 9 pin to 8 pin).
Configure RSLinx the same as you would for your ML1500 DF1 protocol.
See pic below for ML1500 to PV cable.
PVCabletoMl1500.jpg
 
HI AGAIN

This is my cenario I have micrologix 1500 1764-LRP and its channel #0 connected to panelview 300 DF1 port through cable 2706-NC13.
I communicate with plc using cable 1761-CBL-PM02 with RSLINX/ laptop but the only problem I have that I can not see panelview on RSLINX. Thanks and waiting for your replies.
 
To be clear, you want to see your ML1500 and the PanelView at the same time while connected to the Ml1500 thru its port Channel 1.
The ML1500 does not support pass-thru. So, no can do.
You would have to have a DH485 PV and one of the ML1500 ports configured for DH485 and a AIC module to do this.
Or maybe a port splitter ( not sure about this one ,never used it)see link.
http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/1747-pp019_-en-p.pdf
See pic below for one way to do it.
OneWayToDoIt.jpg
 
Last edited:
HI MICKY

Thanks for the fast reply and now I understand why I can not see the pv but if I want to only upload/download the panelview file using panel builder 32 do I have to refer to you previous post or there is other alternative. Thanks again
 
PERSPOLIS said:
HI MICKY

Thanks for the fast reply and now I understand why I can not see the pv but if I want to only upload/download the panelview file using panel builder 32 do I have to refer to you previous post or there is other alternative. Thanks again

There only one way to do it. Use that cable you referred to above ( 2706-NC13) its a straight thru cable. Disconnet it from the ML1500 and connect it to your PC/laptop. Or check out that port splitter above, again not sure about it.
 

Similar Topics

Good morning, I would have a question to ask you. I have a Micrologix 1100 to which I have to connect a PanelView C300 in ethernet. I have...
Replies
9
Views
2,079
Hi, we are using PV300 and using Panel Builder 32 as software. We are receiving the error code as 31. Please let us know how to clear this error.
Replies
3
Views
7,935
i have a panel view 300 whos cat no. is 2711-k3a5l1 i am using comm'' cable 2711-nc13(rs232)cable when i connect it to pc and pv 300 after that i...
Replies
12
Views
7,834
Hello all, I have a panel View300 - Model: 2711-K3A17L1 B A 4.41 (AB) By connecting it shows me 'ERROR 40' - Manual Error 40: Error firmware (...
Replies
3
Views
5,261
Hello everyone! I'm trying to hook up two HMI(panel view 300) to the same PLC (micro logix 1500) using the same port as the other port is connect...
Replies
5
Views
3,488
Back
Top Bottom