RSLogix500 Pro, 5/05 Decompiler CRC?

OkiePC

Lifetime Supporting Member
Join Date
Mar 2005
Location
ENE of Nowhere Oklahoma
Posts
11,791
RSLogix500 v7.10 (cpr 7)
1747-L553C Series C Firmware 10 Revision 5

This is a fairly heavily loaded SLC with lots of DeviceNet and considerable ethernet communications going on. It controls a large beef grinding operation.

About a dozen times over a period of 3 years, during extensive online editing, the CRC somehow gets corrupted.

When trying to save the file, we will get an error:

Upload Failed!
Decompiler -> CRC of executable code does not match
Decompiler -> CRC of executable code does not match
(Yes, it repeats the error twice in the dialog box, followed by an OK button)

Once this occurs, the processor will not allow an online connection. You cannot upload to a new file, you can only download.

The process it is controlling will continue to run fine for anywhere from 5 to 8 hours and then the system will fail reportedly losing communication to the HMI, and strange behavior occurs on the devicenet.

It was reported to me that "conveyors won't stop until we hit an e-stop button". I am not sure how the drives are programmed to react to devicenet failures or whether the devicenet ever detects a fault.

Yesterday was the first I had heard about this problem which is on a system my counterpart takes care of, so I thought I would search the know base and forums and see if we can figure out what is going on.

A/B simply says to download a fresh program, which will shut down half our plant for a half hour so Mike usually waits until production ends, or when the system finally dies, he can log in from home and dump the program into it.

He says this only happens when doing online editing, and he thinks he could reproduce by doing lots of editing too fast.

Any ideas? Especially the part about runing for 5 hours after we get the error...that is very, very weird...
 
One thing we ran into this week infact was that the processor would fault out, the ethernet would fault (so you couldn't clear any faults until you power cycled the processor). What we found was the processor can only handle 8 "connections" through ethernet anyways, at one time. So RsLinx to your computer, any calls from servers, any calls from Operator Panels, MSG blocks etc, count toward this 8. So if your edit computer is only hooked up during edits, then it happens to get a "call" from somewhere during this time -- could be an issue.


George
 

Similar Topics

So here's my situation, I have been tasked with modifying the logic to mimic a button press in the PLC. I have two identical machines however one...
Replies
6
Views
538
Hello, I'm new to programming. I'm using RSLogix500 to modify an existing program for a SLC500. My plan was to use one of the existing inputs...
Replies
26
Views
1,983
So i have an allen bradley rack (2080-LC50-24QWB), i have it connected through ethernet. I dont have an offline program so im trying to upload...
Replies
6
Views
677
Hi Everyone, I am supporting a system which runs on a SLC 500 (1747-L532). A fault has developed whereby the output state of some digital outputs...
Replies
10
Views
997
Hello, I am currently taking a course on plc programming and in the course rslogix 500 is being used. I am however having a problem since it keeps...
Replies
4
Views
1,698
Back
Top Bottom