salman111a
Member
We are still facing a problem regarding communication loss in PLC-5/40L with 1771-ASB Adaptors (8 chassis and with single slot addressing we have racks 2 to 17 in REmote IOs) as described below
NATURE OF PROBLEM
1- The systems goes to faulted state frequently
2- The major error code we receive is S:12=83 “Watchdog timer error”. And the bits S11 gets status 0000-0001-0000-0000 (this inidicates only watchdog timer error)
3- All the Remote IO communication module loss communication as soon as this fault occurs.
4- This fault is removed as soon as we recycle the power.
TROUBLESHOOTING ACTIVITES DONE:
1- The scan time of PLC-5 was increased from 500ms to maximum (due to this frequency of fault has decreased but it’s still there).
2- The fault routine was developed in which as soon as this fault occurs the system goes to this fault routine and find the status of error . If error code matches the fault code 83
The system removes the fault . Due to this now as soon as this fault comes the PLC don’t go in fault state but the Remote IOs goes in non-responding state again. This is
recovered at once only by recycling power.
3- All the Remote IO cables were checked and if there was some error in cables then the system must not get OK at once after power up.
4- The configuration of Remote IO adaptors is changed from manual startup to Auto Startup after fault.
But still the problem is same. Is there any remedy for it?
NATURE OF PROBLEM
1- The systems goes to faulted state frequently
2- The major error code we receive is S:12=83 “Watchdog timer error”. And the bits S11 gets status 0000-0001-0000-0000 (this inidicates only watchdog timer error)
3- All the Remote IO communication module loss communication as soon as this fault occurs.
4- This fault is removed as soon as we recycle the power.
TROUBLESHOOTING ACTIVITES DONE:
1- The scan time of PLC-5 was increased from 500ms to maximum (due to this frequency of fault has decreased but it’s still there).
2- The fault routine was developed in which as soon as this fault occurs the system goes to this fault routine and find the status of error . If error code matches the fault code 83
The system removes the fault . Due to this now as soon as this fault comes the PLC don’t go in fault state but the Remote IOs goes in non-responding state again. This is
recovered at once only by recycling power.
3- All the Remote IO cables were checked and if there was some error in cables then the system must not get OK at once after power up.
4- The configuration of Remote IO adaptors is changed from manual startup to Auto Startup after fault.
But still the problem is same. Is there any remedy for it?