I was wondering if anyone had experience with a PLC5/20 and the PID instruction faulting the processor while changing values in the setup screen.
I was programming online and I noticed that the PV for the PID loop was reading double what the instrument was. I figured it must be scaling so I opened the setup screen , and I changed the low raw value (from 0 to 819), then the processor went into fault.
The error was something like "illegal setpoint" or "setpoint out of range". I change the low value back to 0 and tried to go online again and it faulted again with the same error.
The only way to clear the fault was to delete the instruction and copy an existing PID controller.
Has anyone experienced this before?
Thanks.
I was programming online and I noticed that the PV for the PID loop was reading double what the instrument was. I figured it must be scaling so I opened the setup screen , and I changed the low raw value (from 0 to 819), then the processor went into fault.
The error was something like "illegal setpoint" or "setpoint out of range". I change the low value back to 0 and tried to go online again and it faulted again with the same error.
The only way to clear the fault was to delete the instruction and copy an existing PID controller.
Has anyone experienced this before?
Thanks.