The setpoint should be compared to the EU range, which in this case is incorrectly configured. The PID block scales the input PV (0-4095) to Engineering Units, and then calculates the error from Set Point. (Also in EU). The print outs show EU of 0-4095, it should be what ever the input scaling is (assume Type J) then 32-1400F.
The bang-bang behavior suggests otherwise, and it depends on how the output is scaled, but with the PV range set to [0-4095] and the temperature in degrees, a 1 degree change is 0.025% of full scale, so 50 is not the most outrageous proportional gain.
Or am I still not grokking the scaling of the PD-based PID?
Going to have to wait till I get there to find out what is true settings.
The screen shots I sent of the PID were from 2011... I ASSUME no one else has been in the logic...
Type K is control...
Has anyone had an issue with a PID control after the processor has been upgraded form a L40E to a L80E. It does not seem to be controlling...
48
6,015
Has anyone ever converted a the PID instruction from a PLC5 to a CLX platform? The issue I am facing concerns the difference between a PID...
3,474
I'm working on a project to convert an old PLC5 processor to an L63. Below is sample logic of one of the several PID controls from the...
5,044
Hey fellas, I'm in the midst of doing my first translation from 5 to 5000 that also includes PID instructions. I'm just looking for any helpful...
5,518
Hello I am troubleshooting a PID. My set output percentage from my SCADA is 60%. However when my PID is in manual my CV is stuck at 20%??? I can...
3,108