The other day had a problem with a machine in which the output card indicator light was on but no 120v at the card. While checking the card I did see 120v for about 2 seconds and it was gone. I figured I had a faulty relay on the card so I switched the card out. Problem is still there--indicator light illuminated no 120v on the terminal. Changed out the rack---still have the problem. Switched to another output on another card. Never saw nothing like this. Any light on this problem would be appreciated. I'm very confused. Thanks to ALL-----Terry
 
You said you changed to another output on another card, what was the result?

Did th trouble follow the field device? If so, the circuit EXTERNAL to the card is probably drawing too much current for the output card to handle. Are you ABSOLUTELY sure the card is "relay out"?

Stationmaster
 
The problem child is O:2/2--switched to O:9/3. Started working. Before doing anything I applied 120v to the wire to verify wiring was good going the the solenoid. Ashort pulse to check it out.

Terry
 
Most interesting..... The only thing that springs to mind would be the output common supplied to that portion of the output card. Are both output cards the same type? #2 and #9?

As far as I know, nothing in the CPU, or program, or rack, should be able to turn on the output indicator led, and NOT turn on the output. That should be a function of the output card, it's common supply, and the load. (you did check for potential at the associated common supply to the card, right?)

If you figure it out, please post the solution....I'm quite curious.

Stationmaster
 
Just shooting from the hip here but, if you had something like this:


Start Stop O:2/2
------| |-------|/|----------------------( )---
| |
| |
| O:2/2 |
---| |---


That somehow got changed to this:

Start Stop O:2/2
------| |-------|/|----------------------( )---
| |
| |
| O:2/2 |
---|/|---



And your scan time was low enough, couldn't that cause the LED to flash fast enough as to appear solid but not allow the relay to close before it is opened again? I've never tried it, but at 11:30PM, it looks right to me.

Also, I would do a cross reference (not find all) on O:2/2. Scroll up in the resulting window and look for anything that may be referencing the whole output word, like a MOV, MVM or COP statement.
 
If it comes back, I would suspect spikes and bad luck on the replacement card more than a programming error, but that is easy enough to rule out.

Have you had any rack faults? I have seen very weird behavior from a 1746-OW16 outputs 7 and 8 which are very near the backplane.

Spikes caused by inductive load were causing backplane noise, misinterpreted by the scanner (remote rack) as the adjacent or undetermined slot faults.

It also resulted in a couple of occurences of the LED not matching the relay state, but this was shortly followed by rack faults. I was able to detect retries and errors on the scanner diagnostic integers only when output points 7 and 8 were fired.

Changing to a triac card and adding surge suppression was the fix in my case. I have seen this twice on isolated systems.

Probably you just got a bad spare card, but it might be useful to measure the peak current draw of the solenoid, verify the surge suppresion, and/or fuse it...but I would not worry about it unless it comes back...

Paul
 
Terry Boblitt said:
Had no faults at all. It's just O:2/2 indicator light was illuminated and no out at the card?? When the line goes downI will dig a little deeper. Thanks to all...[/QUOTE
Is it possible that your output device "drains" all the juice the card can provide through its output??
EDIT: Just saw Stationmasters reply.
I am with him on this one!
Can't think of anything else!
 
When you changed the output card did you change out the terminal block? Doesn’t happen very often but I have seen it once where the block was missed up.
 

Similar Topics

Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
Replies
5
Views
198
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
Replies
1
Views
1,035
Happy Friday everyone! I recently installed a new module, 1746 NIO4I, into the last slot on this chassis. Got the normal IO mismatch fault, added...
Replies
5
Views
1,588
Does anyone know where to get either new or aftermarket 1746-N3 connectors and cables for SLC 32 point discrete in cards? I have a used MCC that...
Replies
1
Views
1,249
I am looking to replace a SLC5/05 processor with an AENTR adapter. Configured the rack in a compactlogix. The connection to all of the cards in...
Replies
5
Views
2,332
Back
Top Bottom