Communication Loss

shoeb

Member
Join Date
Sep 2008
Location
NAGPUR
Posts
13
Communication Between Flexlogix Controller And Rsview32 Scada Losses Oftenly ,1762-net-eni Used For Communication.
 
Generic devices: Check all connections, do not terminate your own RJ-45's, use a decent punchdown receptacle and commercial patch cords. Check power supplies.

NET-ENI? Seriously reduce your polling rate (if using RSLinx Classic).

How many tags are being always polled? (Open screens, Alarms, Historical, Event, Derived, etc)
 
POLLING RATE IS 2000 ms,nearabout 500 tags are used.
In Scada RSView32 activity bar Ireceieve a message 'RS LINX ,OPC SERVER BAD QUALITY'
 
Quick estimate would be that you are trying to transfer about 40,000 bits per second. The ENI can't handle that.

Try changing the polling rate to something like 10,000 ms, and see if the bad quality messages go away (this is a test).
 

Similar Topics

Communication between devices will stop working for a certain period of time. I caught the error message using WireShark. I cannot identify the...
Replies
0
Views
101
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
Replies
5
Views
289
Hi, strange issue with Emerson/GE CPE330, i downloaded some new logic into PLC, everything was built properly and downloaded, but when download...
Replies
3
Views
1,020
Hello everyone, Currently I am trying to find an answer for the following situation. I have digital output and input cards connected to the...
Replies
5
Views
1,050
My HP laptop will lose communication with Mitsubishi PLC occasionally after removing ethernet cable to download from WiFi. Our company limits the...
Replies
6
Views
2,164
Back
Top Bottom