I am using a MicroLogix 1500 and am in need of help with using a master line speed and ratios for each output. 10v will=1000 so I came up with line speed*ratio/1000 will = output Just wanted to now if I am working in the right direction.
 
in the SLC 500 instruction set lookup the command SCP and SCL it provides several formulas for linear scaling

y=mx+b
where Y=scaled output
m=slope=(scaled max-scaled min)/input max-input min)
x=input value
b=offset(y intercept)=scaled min-(input min x m)

scaled value=(input value*rate)+offset
rate=(scaled max-scaled min)/(input max-input min)
offset=scaled min-(input min*rate
now you also have to check what range is used for your analog
for 0-10 volt range is 0-32767
for 4-20 ma range is 6242 to31208

attached is an article by Ron Beaufort on scaling
 
appears the file is now too big for this site if yo do a search on Rons posts he goes into more depth I beleive the post was entitled
Y=mx=b
 

Similar Topics

Hi, I have a bit of PLC experience in Siemens and have unfortunately been blessed with working on Automation Studio and B&R which has been a big...
Replies
5
Views
1,392
We have an omron CJ2M-CPU12 PLC that we are having issues with an AD04U analog card. it is connected to a K type thermocouple sensor. The card is...
Replies
4
Views
622
Hi all, While i am not new to omron, i'm totally new to the analog part and lost. i have a CJ2M cpu 33. then there are 4 i/o cards card 5 is a...
Replies
26
Views
2,678
Hi I have a modicon 984 with proworx 32 that is scaling an analog input, and I need to adjust the scaling. I have new analog input values and %...
Replies
3
Views
1,745
I have a Mitsubishi FX2N-64MR-UA1 processor. The 1st analog output card is an FX2N-4DA. It requires 24VDC power. That card is obsolete. The card...
Replies
1
Views
1,607
Back
Top Bottom