...the question of whether RSLinx Gateway is literally running in Gateway mode or running as a Remote OPC...
Thanks guys for your comments.
The application is running through The RSL-G acting as an OPC Server.
Furthermore, we have on this Server, the Gateway/OPC program AND also TrendX which log about 500 Tags to the second.
We have a manage switch
The network is at 100MB
When all PCs(9) are ON-LINE, the most traffic we get out of a pipe is 17%.
Dumb but simple observation is...
When I look into a local RSLinx and I click the Gateway link, It takes 9 second to SEE the status of the 3 connected PLCs.
When I click the direct Ethernet driver to see the same thing... it takes only 4 seconds.
So the direct link IS way faster... unless we shutdown the OPC server and then the RSViews fall unto the direct driver link... then its very slow... in the range of 10 seconds.
When I monitor some Encoders connected to a VHSC modules on the main rack, in RSView Tag monitors, I see there value change every second. It look very fast to me.
The problem or should I say challenges is that when we are running the RSView32 application, the screens just dont show up when they are commanded to do so... before 1 second, and then the values are shown after another 3 to 5 seconds.
Also, the logs are on the Server, so alarms are somewhat slow to appear.
For the MSG, they are continuous. 4 WORDS READ from the 3 PLCs to there 2 other conterparts. And this is VERY slow to show on the RSView but VERY fast between the PLCs.
I have started to cleanup the SCADA applicatio.
First I installed 4 new Quad Core PCs in the main control room with XP Pro and 4 Gig of RAM with FAST HD.
They all have Dual Screens. So 4 PC + 8 Screens
I have leaned up the TrendX setup. Removing ALL but 1 Trend in each PCs AND leaving all the other trend for a PC dedicated to the Managers.
Also I have remove a lot of unused Tags.
------------------------------------------------
My main challenge is finding what is slowing us down.
I see the com between the PC and the PLC is FAST when ONLY one PC is live.
Then , passing through the OPC server must be (for the PLC) no more traffic if 1 PC or 100 PC.
Now when I have 10 PC through the OPC Server... why would there screen appear slow to update?
Again... the ethernet is only up to 17%...