Off Topic, need RPM sensor for very slow shaft
Ken Moore
May 2004
North, West, South Carolina
3,475
Hi folks,
I have a hydraulically driven rake in a clarifier that rotates at about .18 rpm.
When there is a process upset, the bed of the clarifier can become quite thick.
When this happens the rake sometimes doesn't turn.
The Clarifier is currently being controlled by a Compact Logix. 1769-L24ER-QBFC1B. I am looking for an off the shelf device that I could install to monitor shaft rotation. I have used a gear tooth and prox in the past, but looking for something pre-fabbed.
Any ideas?
What about simple prox switch, as slow as speed is that would work with about any PLC input or could you use a zero speed sensor, I forget the brand name(corny name they had but worked great and very easy install) but we used a lot on conveyors many conveyors in a row critical to know if one drop so no pile ups.
We put magnet on shaft end and the entire sensor attached that way with a strap so it would not rotate, it gave a pulse.
Most of the clarifier drives I've seen have a prox like AkaHammer suggested, which is used to detect the movement of the clarifier arm (not on the gearbox shaft, but on the end of the arm at one point on the radius of the clarifier.
We also used to have a torque switch fitted for the DOL motor ones, i think it was just a 3 phase current monitoring device but it's been a long time since I've looked at one.
More recently, as we now drive most with a VSD, I use the built in high torque monitoring feature of the ATV6xx to raise an alarm.
They make (forgot the brand) shaft verifying prox monitors they were not real expensive but you could set the RPMs with a pot to give you a digital input... we had them on our fan shafts that way if the belts broke you could detect it, but I agree just about any prox would work at that speed
I wondered about this too. We did this for a customer last year. Any downsides to this method?
It can be a bit fiddly to set up right, especially if the torque available through the gearbox is high, but the motor runs lightly loaded. I would set it close to the running torque then increase up slightly if there were any nuisance trips. Very hard to see what's going on at the bottom of a deep, sludge blanket-filled clarifier so you always have to hope that nothing starts going wrong early on and you don't end up compensating for a legitimate issue.
Hi folks,
Any ideas?
Do you have access to an open bearing on the final drive? Without that, it's tough to mount an off-the-shelf unit.
Any existing brackets that can be used to mount it? Size restrictions? What power is available (24VDC, 120 VAC, 250 VAC)?
What sort of interface do you have on your PLC to accept the result - Digital input, active low or hi, analog 4-20mA for speed ... I can't think of any others right now ;)
Use a prox and have the rising edge reset a timer. It should get triggered every 5.55min. So if the timer gets to say 12mins (or some value you can live with) you know that something is wrong.
Many of the clarifiers we come across have an assembly that lets the drive chain pop out of place to prevent breaking the rake. Those usually have some sort of limit switch attached that is supposed to be wired into the motor controller or at least to an alarm lamp. 90% of them are either defeated or out of adjustment. If that switch exists and is set up correctly it should function to give you instant notification of a mechanical drive problem.
I've used those. I think they're called Whirligigs.
A standard encoder... or absolute if the system has power cycles and you need to detect if it's moved since.
This is the motor nameplate from one of the powder hoist motors on the USS Texas an older generation battle ship, built in 1911-1914 ish. The...
295
Totally off topic, but strange observation. I purchased a few cisco ethernet switches off of ebay some years ago. They are part of a home lab...
2,079
Good morning, Please excuse me if this is too off topic here, but it is a programmable controller of sort. I have an Omron ES100P temperature...
2,342
Which way is up and what's that strange looking bug? I was trying to login to micro_cr*p team_Shi* and it wouldn't let me because I exhibited...
2,704
personally I don't care about golf - but this is one impressive shot ... if it weren't on tape, I wouldn't have believed it ... the first video in...
1,503