bwiring Member B Join Date Nov 2005 Location mpls. mn. Posts 66 Jan 24, 2009 #1 when using a micrologix and programing a 4-20ma input does 4ma input = a value of 0 and 20ma = 32767 or is 4ma = 20% of 32767.
when using a micrologix and programing a 4-20ma input does 4ma input = a value of 0 and 20ma = 32767 or is 4ma = 20% of 32767.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Jan 24, 2009 #2 More info. Which MicroLogix do you have, complete catalog number? Which analog input card are you using,if any?
More info. Which MicroLogix do you have, complete catalog number? Which analog input card are you using,if any?
bwiring Member OP B Join Date Nov 2005 Location mpls. mn. Posts 66 Jan 24, 2009 #3 ml1100,1763-l16bwa......1762-if4(4-20ma)
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Jan 24, 2009 #4 bwiring said: ml1100,1763-l16bwa......1762-if4(4-20ma) Click to expand... See PDF below for data format of your card. Data will depend on how the card is configured. Raw/Proportional or Scaled for PID
bwiring said: ml1100,1763-l16bwa......1762-if4(4-20ma) Click to expand... See PDF below for data format of your card. Data will depend on how the card is configured. Raw/Proportional or Scaled for PID
bwiring Member OP B Join Date Nov 2005 Location mpls. mn. Posts 66 Jan 25, 2009 #5 Mickey, thanks a lot............just what i was looking for.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Jan 25, 2009 #6 bwiring said: Mickey, thanks a lot............just what i was looking for. Click to expand... Your Welcome.