My question is if the two racks lose communication, will the outputs on the remote rack with NO processor shut off? I know you can configure the output card how to act on a fault etc.., but what happens if there is no processor in that rack?

TIA,

Greg
 
The I/O cards get their communication fault behavior configuration information when the controller establishes the connection to them over the network. You'll see this in RSLogix 5000 in the module configuration window, on the "Configuration" or "Output State" tab.

If the connection fails because of a failure of the controller, the first bridge module, the network, or the second bridge module, then the I/O module will take the action configured in that tab.

If the power is cycled to the chassis but a Connection is never made to the controller, then the modules will remain unconfigured and outputs will remain off.
 
Thanks for clarifying Ken. I have the outputs configured to be "off" in both program and fault mode cases. Just wasn't sure if the I/O had the closed loop communication check back to the processor in the main rack to shut off in this case where there is no processor in the remote rack.

Greg
 

Similar Topics

Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
Replies
4
Views
223
An outside contracting firm designed a machine for our company. There are several devices connected through Ethernet/IP. This includes a Panel...
Replies
4
Views
199
I am getting random comm loss (error code 561 i think?) anyway i looked it up and its loss of comm to 2 modules on a controlnet network. The 2...
Replies
0
Views
358
Hey everyone! I'm searching for an example demonstrating how to program in Studio 5000 speed control of a PowerFlex 525 drive via Ethernet. While...
Replies
1
Views
664
Hello, So I was asked to turn up the speed on a VFD to allow a carriage to move a little bit faster and avoid getting stuck. Im not sure the exact...
Replies
2
Views
753
Back
Top Bottom