Wago DNET Fieldbus Coupler

curlyandshemp

Lifetime Supporting Member
Join Date
Jul 2005
Location
Toronto
Posts
1,903
Anyone use the Wago DNET coupler, part # 750-306?

I plan on using this coupler to resuse some existing Wago I/O blocks that are currently on Profibus and are to be relocated onto an existing Controligix with a 1756-DNB


My concern is if I need anything other RsNetworx for Dnet and the EDS files, to setup up and configure the fieldbus coupler.
 
Generally not to many issues just add the wago coupler to the scan list and configure the polled io with your number of input module bytes + 1 byte for the coupler status, and number of output module bytes.
 