What is the easiest way for a ControlLogix system to have more than a 17 slot local rack ?

I need to have about 29 I/O cards (and it may well be 35 when I'm done), all in the same control panel and just one cpu card.

I don't see any way to link two or more racks?
 
They really don't link together as an "extended local rack" like the SLC does.

I would use a 1756-CNBT in each rack, linking them together via ControlNet. I have a system with 12 racks all linked together this way.
 
Personally I'd have my Controllogix rack only have communication cards then use flex I/O on ControlNet as OZEE Mentioned for all the IO.

That is going to be one heck of a cabinet.
 
As Ozee mentioned you can use the 1756-CNB or 1756-CN2 (newer version) and hook the chassis' together using ControlNet. ControlNet may be more than you want to tackle though.

You can also do the same thing using EtherNet/IP. The 1756-ENBT or 1756-EN2T (new higher performance version).

Either way, you add that module to your local chassis and then add a similar module in the remote chassis. As mentioned, you might go with a small chassis for the controller and comm card and then use Flex I/O for all of the remote.

** EDIT ** Ken typed faster than I did!!

OG
 
If it was me I would stick to ethernet/IP. I have converted all my systems over to Ethernet/IP including VFD's. It was very easy and I didn't need to buy ControlNet software!

Flex I/O works well for remote racks. I have several connected over an Esteem wireless network. (Nothing very critical!)

Kevin
 

Similar Topics

I would like to use the external clock source function to display time on a 15" C-more EA9 panel. The source would be a Logix processor. When I...
Replies
2
Views
1,347
Partial disclaimer: I'm not the one programming the radios so everything is suspect. But I need to get the CLX eliminated as a problem. I will...
Replies
3
Views
3,427
Does anyone know if it is a nescesity to use rs-485 with the modbus slave program (that can be found in the rslogix project folder)? Or will a...
Replies
0
Views
1,482
Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
Replies
0
Views
195
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
420
Back
Top Bottom