Who makes the best air power coolers? I have been looking at exair brand
http://www.exair.com/en-us/Pages/default.aspx as well as vortec
http://www.vortec.com/vortex_ac.php
I just wanted to get some opinions from people that use these.
Are they typicaly better than an ac unit for a enclosure?
Our ac units do not perform that well because the plant is so hot also.
Kid
Any chiller can create condensation of atmospheric water on its exterior surfaces. ASSUME you will get water on surface install and put in a drain to make the water go where YOU want it to go.
METHOD -------- INSTALL -------- OPERATING -------- MAINT
-----------------COST ---------- COST ------------- COST
Fan w filter -----low -----------low ------------- medium
vortec -----------low ---------- high ------------- low
chilled --------- low/med --------low ------------- med
water (assuming you have chiller unit already)
Integral ---------- high --------- low/med -------- medium
A/C
Vortec is a hog of a plants most expensive utility - compressed air however if you are space limited may be only option. Watch out for condensation and for water in the air - run exhaust air outside the cabinet
Fan and filter service life depends on how much dust and other contaminants get in fan. Filters must be small enough to filter out nuisances. Most effective when this puts a positive pressure on cabinet thus leaks go from inside to out and reduce dust loading inside cabinet. CHANGE FILTERS pain in xxx and management squaks over cost. Will not be very effective if area temperatures are high ie over maybe 85 to 90?
Chilled water may be prettty inexpensive to install if lines are already in immediate area. Antifreeze will help to reduce corrosion so will additives - jacks costs - another maintenance item.
WATCH OUT FOR CONDENSATION IF SYSTEM TEMP
< 45 or 50 espeicially in high relative humidity climate.
Integral air conditioning ie heat pump air to air. works very well - high install cost - life cycle about 10 years or so on compressor, power draw between 250 watt to 1Kw depending on size. Will not work well if area temps very high ie 95 plus (condensor efficiency inverse proportional to area temp)
WATCH OUT FOR CONDENSATION ON EVAPORATOR (the "cold portion" inside cabinet) you WILL get condensation.
Dan Bentler