Multiple 480 contactors in one enclosure

PeeEeLSee

Member
Join Date
Feb 2024
Location
Midwest
Posts
1
Hello all,

I have a question and would like a few opinions if possible. 5x 480 outlets control 5 machine. I want to run them through a contactor each and having PLC control when its able to have power. Any big safety concern in shoving all 5 contactors in a quite medium-large sized enclosure? Will be having 5 line going into the box from these 5 outlets and 5 load back out of the enclosure and into the machines.

Thanks again.
 
Should be no issue....contactors are electromechanical devices, so no real concern about heat dissipation of electronics. Try to keep wire entry and exit space above and below contractors reasonable for maintenance purposes, but other than that, should be fine.
 

Similar Topics

This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
146
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
489
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
Replies
8
Views
316
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
Replies
1
Views
125
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
Replies
2
Views
167
Back
Top Bottom