hiii
my plc is omron cpu cqm1h, when make change in my program on line ,program work ok and after plc power turn off and retain to turn on my changes are cancelled and program retain to its original program ,
i want whate is the reason
 
I don't use the CQM1H, so I don't have any Manuals here for them.
However, it sounds like it is reloading the program from an EPROM, or a Flash Card mounted in the PLC.
Have a look at the manual, see if you have an on of those in the PLC, and the procedure for writing your changes to it if you want to make the changes permanent.

Hope that helps.

Stu.....
 
Dip Switch Setting

Check your dip switch setting for number 5. I had the same problem some time back. I think if it is in the ON postiion the program reloads from its MMC card at power up. When it is in the OFF position it will be held with the battery back up. If this is not it check your battery.

Good luck and let me kow how it turns out.
 
On the CQM1H, you have to save the any changes to the program, to the EEPROM by forcing bit A14.00 ON while in the PROGRAM mode.

Turning DIP switch #2 to the ON or left position forces the CPU to load the program from the EEPROM into RAM upon powering up the PLC.

If you have not saved the program, then you will get the original program and lose your changes.

Turning DIP #2 to the right or OFF position does not reload the program from the EEPROM and therefore will operate with the most recent changes in RAM but that is not a good long term solution since if you were to lose power and the battery is dead, you will not have a program to run.
 

Similar Topics

Hi Everyone, I have a customer that needs a CQM1H (CPU51) replaced. They purchased the processor new-old-stock from a source they found online...
Replies
3
Views
360
I have an Omron CQM1H-CPU21 and a NS8-TV00B-V1, I have followed the manufacturer's spec on how to set this up and all I got is the HMI is trying...
Replies
7
Views
892
Hello maybe someone can help me, I have omron CQM1H PLC with CLK21 (Controller link module) and SCB41 (Serial module connected with NMB CSD-891B...
Replies
1
Views
548
I need a CQM1H-CPU51 to talk to my Red lion Da30D i just need to read the status of some I/O and maybe read some data registers but I cannot...
Replies
7
Views
1,166
Hello, I need some help to convert PMCR instruction from Omron CQM1H that using CQM1H-SCB41 to CJ2M using CJ1W-SCU4, The problem is on the old...
Replies
1
Views
851
Back
Top Bottom