I want to know about GE 90-70 CPU redundancy. Please guide me which Hardwares it would require? how H/W config has to made and how Cpu redundancy is established.

any Sample program?? welland good or U can explain me in detail.

Thanks in advance
 
Fro 90-70 Redundancy you need, 2 Racks, 2 CGR Redundancy CPU's, 2 Redundancy Communications Modules (RCM), 2 Bus Transmitter Modules (BTM), 2 BTM to RCM connection cables and 2 modules for however you are going to control I/O, mostly either GENIUS or Ethernet to ENIU's.

Redundancy is configured with Proficy Machine Edition software. The same exact logic goes into both controllers but they have seperate configurations as one is Primary, the other Secondary.

Transfer between controllers is bump and seamless. It works, I have setup over 100 of these with virtually no issues. For more info, go to support.gefanuc.com and search for 90-70 Redundancy and GENIUS Global Modular Redundancy (GMR).
 

Similar Topics

Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
84
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
194
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
80
Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
Replies
10
Views
379
Hi Guys, Is it okay to have Redundancy ControlLogix Processor IP address set to DHCP? I had Static IP address on it but removed it via RSLinx...