1769-if8

There's a Module Profile for the 1769-IF8 module in RSLogix 5000 v16 and later.

You don't need to "program" the module, just set up its configuration settings in the configuration applet.

Are you using an older version of RSLogix 5000, or have you somehow not installed the Module Profile for this module ?
 
I haven't found where you can do the scaling in the module config. Am I missing something? Can the scaling be done in the module configuration or do you have to do it in the program?
 
You're not missing anything, Jim. The original poster asked how to "set up" the module, which I interpreted as configuring the voltage or current range, the filters, and the alarms.

The 1769-series modules do not have some of the features of 1756-series modules, including onboard scaling to engineering units, or rate alarms.

The 1769-series modules are most similar to their SLC-500 counterparts, with scaling options limited to Raw, Engineering Units, Scaled to PID, and Percentage. "Engineering Units", in this context, really means "measurement units" because it outputs a value that corresponds to Volts or Milliamperes (i.e. 4000 for 4 mA, 20,000 for 20 mA).

The 1769-IF8 only recently got a good I/O profile in RSLogix 5000. There are Knowledgebase documents that describe how to run the module using Generic configurations, such as Answer ID # 28460.

Scaling the input data into true Engineering Units, like Feet Per Second, Gallons Per Hour, or Furlongs per Fortnight requires some controller logic. Use the SCL instruction in Function Block language, or do a simple linear equation in Relay Ladder Logic.
 

Similar Topics

Hey guys, Been a while, I have an odd one. Something that should be straightforward. I have a 1769-IF8 module, looking to add an analog, been in...
Replies
13
Views
4,497
my customer has a full 1769-compactlogix rack. they want to remove the two cards in slot 5 and slot 6 and replace them with two new cards. The...
Replies
4
Views
1,593
Hello! I have a project, use the software is studio 5000 v30, the 1769-L30ER compactlogix controller, 1769-LIF8 1769-IQ16 and 1769-OB16 modules...
Replies
3
Views
1,895
Hi folks, The 1769-IF8 has a ChannelStatus Bit, do you use it? From my reading of the manual, this bit is set when the channel has one of many...
Replies
5
Views
2,290
Can a analog card properties settings such as RTS and filter frequency can be changed with CPU in run mode without causing errors or issues...
Replies
2
Views
1,905
Back
Top Bottom