parameter access in s7-300 with 22-comm-p

ragavi

Member
Join Date
Nov 2004
Posts
5
can any body help me to Reading/writting drive pf40 parameters through profibus network.

i have S7-300 plc. cpu 315-2dp connected in profibus via 22-comm-p and power flex 40 drive.

in my hardware configuration i have configured the parameter access module.

i have written the programe to read the parameter

request--->response -----> 0---->0

when send read parameter 22. the following response i am getting. i think this not correct.

request word 1 = 2#0001_0000_0001_0110

response word 1= 2#0001_0000_0111_0110

help me to read the correct parameter.
o_O
 
i have found that the bytes were getting swapped. so changed the jumper J3 in 22-comm-p to lower position then the problem got solved.
 

Similar Topics

Greetings, I am working on a project and I would like to scale %AI to -10.0 to 10.0 VDC. The module Input data is stored as a 16 bit Integer and...
Replies
4
Views
71
I'm trying to change some of the parameters on a Yamaha SR1-X-05 robot servo via RS-232, but the unit isn't letting me change them. I can use...
Replies
0
Views
374
Hello, I'm working on a program I migrated from S7 v5.6 to TIA v14. I am failing the consistency checks on my safety program with the following...
Replies
20
Views
4,549
Compactlogix PLC I have a totalizator function block that totals flow. There are unusual circumstances where we pause flow momentarily and the...
Replies
5
Views
1,600
Hello, I want to know if it's ok to access the memory of an instance DB (ex. instance DB100 of the FB100 - defined as static parameter in this...
Replies
4
Views
3,664
Back
Top Bottom