oops, can I do it?

ltfordnr

Member
Join Date
Aug 2007
Location
seattle
Posts
36
D2 250-1
Need configure for ModBus Master and get messages R/W from other equipment on network.
This ain't like the Logix I'm used to.
Like learning a new trade.
Any Quick tips?

Thanks
 
Sure you can, but it's a H$LL of a lot easier with a DL260 which has built in MODBUS commands.

I have a set of instructions for dealing with some drives over MODBUS here. Of course it's probably not the equipment you are dealing with. Ignore page 5 - it's what you would get with a DL260.

Instead look at the references in the manual available here
especially those in chapter 4. You'll have to set the port to MODBUS and then (and this is the bad part) translate the external MODBUS reference into the equivalent AD CPU references.

For help on that refer to AN-MISC-009 and AN-MISC-010 available here.

As I said, get a DL260 CPU. See you when you get done.
 
Thanks Berie, I was thinkin' the same thing. I thought it would be lovely to use a spare 250-1 but alas, I now see the investment in a 260 would be the way to go. I was ready to do some creative networking and general trickery to overcome the 422 issue as well but with the 260 it will be much more streamlined.
Thanks for the time,
ltfordnr:sick:
 

Similar Topics

I´ve being trying wrap head around FOR loops.. When and what can this be used for? I´ve mostly seen it move data, resettting arrays etc. I made a...
Replies
2
Views
12
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
Replies
7
Views
821
Hello Everyone, I have about 135 controller PIDE loops that I need to add to my Studio 5000 and that means I will probably have to create about...
Replies
8
Views
1,948
Good morning, I am currently having a struggle of getting cascaded pide loops to work within studio 5000. I have read and followed all the...
Replies
5
Views
1,940
Hi all, I hope everyone is well, I am in need of something so simple, I have made a small program in SCL and want to monitor some loops in...
Replies
5
Views
4,498
Back
Top Bottom