PLC Kid, in the world of NEMA motors, those 25hp and smaller are generally wound wye. Above 25hp, the norm is delta.
Where NEMA motor differ from IEC motors is that NEMA dual winds the pole coils so, in parallel, they are 230V and in series they are 460V. The standard IEC practice is to single wind each pole but bring out to the junction box both ends of each coil (six leads). For 230V, the coils are connected in delta, for 400V, the coils are connected in wye.
What makes the IEC system work is the fact that the two common voltages are 230/400 which is a ratio of 1.73 or the square root of three. In the NEMA world, the two common voltages are 230/460 which is a ratio of 2.00. That forces the windings to be different.