lordloverocket
Member
- Join Date
- Dec 2003
- Posts
- 24
Has anyone ever encountered a watchdog timer error on the micrologix 1000. Our plant recently had a planned power shut-down which meant that we ran on generators for several hours. The unit in question was showing the fault LED when power was restored and when cheching the cause of the error I discovered that the watchdog timer had timed out. I have checked the scan time which shows a max recorded scan of 1 mS when running and the max allowed was set to 50mS. I have increased this to the maximum that is allowed, 255mS I think,but i can't understand the cause of the fault. The program isn't complex and there are no jumps or loops, could the PLC be faulty? Here's a rough copy of the program. Is there any code that will allow me to reset these types of error automatically without the need to connect a pc? Again I would like to thank you guy's for any help you can give me
T1/DN I1/0 I1/1 T1
_____________
--------¦/¦------¦ ¦----¦ ¦-------¦ ¦
¦ ¦
¦ ¦
¦ 5 sec ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦____________¦
T1/DN SQO
_____________
--------¦/¦-----------------------¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦____________¦
I1/0 I1/1 MOV
_____________
--------¦/¦---------¦/¦-----------¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦ ¦
¦____________¦