Now i configured my s7 200..... in my program i have to get some signals from another plc.. so can u tell how to perform the profibus communication between the plc's.... i found it for 300 but cant in 200 .... so pl guide me
 
An S7-200 can only be used a Profibus Slave, It can not be used as a Profibus Mater. You can use PPI or Modbus to talk between 2 S7-200
 
hi ,

For analog program u need "SCALE" library

c the attached library file & Use itr function.

Regards,

Nelliyan.G
 
An S7-200 can only be used a Profibus Slave, It can not be used as a Profibus Mater. You can use PPI or Modbus to talk between 2 S7-200

Profibus slave only by using a em277 module not by local ports

but right, s7-200 to s7-200 comm is only thru PPI Siemens Protocol or building a modbus RTU Master slave small network...
Or maybe by adding an expensive ethernet module on each but it is probably better cost efficient to discard s7-200 and use newer s71200 in this case with the built in ethernet port...
 

Similar Topics

Hi. I have a 222 CPU. I need to recover the program from the eeprom memory. Is it possible?
Replies
1
Views
82
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
252
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
81
Hi folk, I would like to know what kind of Parameters should I setup for controlling with Profibus. My old Lenze 8200 motec 0.25kW have a busted...
Replies
0
Views
79
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
Replies
4
Views
118
Back
Top Bottom