The way I do it is to place the Parameter Numbers of the parameters that you want to monitor into Parameters 61, 62, 63, and 64.
(I mis-identified those earlier as 81-84. They are correct, of course, in the EDS and User Manual).
Those four parameters will then comprise the 8-byte Input connection.
For example,
Parameter 61 = 21 Device Status
Parameter 62 = 15 Warning Status
Parameter 63 = 14 Trip Status
Parameter 64 = 4 Average Current
The Device Status includes the 4 Digital Inputs, the two Output Relays, as well as whether the device is in a Warning or Fault condition.