Does anyone know if you can replace hardwired interlocks (high gas, low gas, fan on, over temp, etc.) for burner management systems with a safety PLC? I have an oven system with multiple zones and this would eliminate a panel full of interlock relays. I'm not trying to replace the BMS, just the interlocks by wiring them straight to safety input cards, series them in the plc and energize a safety output to the BMS. From this old thread it appears not but 8 years later, I'm hoping there's changes where you can use a safety plc without all the red tapes.
 
The major question is how your system is governed by NFPA 86, the "Burner Code".

There was a good post on the topic a while ago, here:

http://forums.mrplc.com/index.php?showtopic=16443

NFPA 86 was updated in 2011 to include a section on programmable controls. If you plan to do this in-house, that's where you have to start.

I think you'll find that some of the functions, like high-gas and overtemperature, still have to be hardwired.

This is one of the few areas where I always defer to a qualified consultant.
 

Similar Topics

How do you install update on Red Lion Crimson ver 3.1. Do I just need to run the exe file on the host server?
Replies
1
Views
107
Hi All, does anyone know is it possible to install BMS-graf-pro v6 without the installation key, I only need to make a small change, is there a...
Replies
0
Views
1,819
Hello all, What is your thoughts about implementing BMS systems using PLCs and SCADA. We did a couple of projects like that with success. I also...
Replies
4
Views
2,061
hi friends. i have PLC with 13 inputs , i want to give the status of these inputs to BMS server guy , he want to read the status through modbus...
Replies
4
Views
3,172
Hi guys, I am planning of shifting from PLC to BMS industry as in my country BMS projects are at their peak right now. Any advice from seasoned...
Replies
0
Views
1,574
Back
Top Bottom