Hi guys, and Gals. I have a Anderson flow meter sending me 10 pulses per liter of water. This is going into a AB CFM module that is calibrated to read also 10 pulses per liter of water.

Sounds simple enough but, our water is actual not equal to 1 liter = 1 KG of water. It is actually 1 liter is = to .966 g/ml of water. What i am trying to figure out is how to convert it into the plc so i have accurate readings.

We are not effected much on product with low volumes of water, but on high volumes we see a problem.

Any help would be great.
 
At the moment you multiply the number of Litres by 1 to get the Kilograms. Instead multiply the number of Litres by 0.966. Otherwise you could adjust the pulses per Litre, but the pulses per Litre is currently correct, it is the Litre to Kilogram ratio that is wrong.
 
Ask anderson if you are correct when the density is lower they will have calibration tables.
So when using another type of liquid the flow meter has to be recalibrated anyhow.
Or do it yourself with a tank etc.
an yes bryan is correct too.
however better to have a calibration number (maybe even a array with different flows like for oil is used.
 
Hi protrac231

Do not forget that density of liquids is dependent on temperature.

In order to get a precise measurement, the media temperature must be taken into consideration.

/fryman
 

Similar Topics

I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
Replies
3
Views
229
Currently I’m using ESA model VT155W0000 HMI and it’s communicate with Fanuc PLC. Can any one suggest can I convert ESA model to EXOR HMI eSMART07M
Replies
0
Views
110
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
Replies
2
Views
142
I have a Type C to RS485 adapter connect to my Siemens RWF55. I use modscan to scan it to get a value from the Siemens controller. In the...
Replies
4
Views
113
Hi all, I'm in the process of upgrading a PanelView1200 HMI program to be developed in FactroyTalk View Studio. The filetype for PanelView 1200...
Replies
7
Views
308
Back
Top Bottom