Can anyone explain about I/O Adapter and Scanner because there is a confusion.On Allen Bradley website it is stated as a I/O Adapter module while on PLC-5 manual it is stated that PLC-5 has both I/O Adapter and Scanner mode.

Does it mean PLC-5 has integrated I/O Adapter and Scanner?

Does I/O Adapter Module also use as a scanner?
 
You didn't mention which PLC-5, but most PLC-5 processors have multiple, configurable, communication ports. So one port could be configured as a Remote I/O scanner, controlling and communicating with multiple remote I/O chassis.

At the same time another port connected to a completely different network could be configured as Remote I/O Adapter.

The PLC-5 could act as an adapter to another scanner PLC. This could allow it to appear as Remote I/O to another PLC. While also scanning it's own Remote I/O.

OG
 
The PLC(processor) typically has several I/O ports that can be setup to communicate in different ways.

Most common is to setup a PLC I/O port as a scanner. The PLC will scan for devices attached to that port and then will Read&Write data to those devices.

If you have IO cards in a rack other than the rack that the PLC processor is in, that "remote rack" will have an Adapter Module. The PLC will see (or scan) this adapter module and Read&Write to it. The adapter module will pass the PLC Write&Reads to/from the IO cards in the remote rack.

As a different scenario(less common), a PLC can also have an IO port setup as an adapter rather than a scanner. In this case, that PLC Port for PLC#1 can be scanned by another PLC(#2) (with a port setup as a scanner) such that PLC#1 port looks like an adapter module to PLC#2.

An I/O Adapter module is always an adapter. Only the PLC can scan.
 

Similar Topics

Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
Replies
6
Views
413
Hi good day Everyone, I have a cimplicity v10 project with 7 to 8k tags communicating with AB PLC through OPC and Rslinx classic. I have this...
Replies
3
Views
219
I am using Allen Bradley PLC 1756-L81E and EIP module 1756-EN2TR for Ethernet/IP communication. My communication works fine but in Get-Attribute...
Replies
2
Views
203
I have a network with 4 PLCs PLC1 is controllogix and PLCs 2-4 are compactlogix and they all need to communicate. The current way I have this...
Replies
8
Views
262
Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
Replies
1
Views
279
Back
Top Bottom