SLC5/05 Slow Ethernet

KEN_KACEL

Member
Join Date
Nov 2002
Location
NORTH COUNTRY
Posts
162
The system has 4 SLC5/05s L553 series C and 8 PV+ HMIs and 1 Versa View Box. There is Fiber and a Hirschmann MICE on the LAN. With all this on the Ethernet LAN the communications has slowed to where the pushbuttons respond very sluggishly, the HMI screen updates take 6 to 10 seconds. Any thoughts to speeding this ethernet system up. The LAN needs to grow by 3 Controllogix 5000 and 6 more PV+ HMIs. What cuases it to slow to a crawl? It takes 1_1/2 hr to save the program through the RSlogix500. AQlso getting "edit error".o_O
 
had simlar issue about a month ago i tried diffent cables about everything you could think of then i did a point to point hook up and promblem went away well anyway to make long story short it was the hub that was bad all lights on hub where blinking like everything was fine but when new hub installed all problems went away hope this helps
 
The SLC has a limited number of connections and all those panelviews may be pushing you to the edge. If you could use one RSLinx Gateway installation to do all the polling of the SLC, then share that via DDE/OPC to the other devices it would reduce the number of required connctions. I am not sure that's possible with the PV+.

If you have spare horsepower in a Logix CPU, you might do better to have it poll the SLC and let the PV+ units read data from it where the connection limit is much greater.

I think you can view the connection statistics in a web browser pointed to the SLC IP address.
 
Make sure S:2/15 is cleared so the 5/05 can service more than one Ethernet comm request per scan. It's like night and day on a sluggish system when that bit is set or not.
 
It can just be set to 0 in the Status File.
Another note: I've monitored the Comms Pending bits (S:2/5 & S:2/7) and executed an SVC instruction as well to try and speed communications up. I "sprinkle" that rung at various points throughout the program scan. Not sure is if it makes a big difference.
 

Similar Topics

I am having a weird experience using KepwareEx6 as an OPC Server for a set of SLC processors where the tag data is not updating remotely at the...
Replies
2
Views
570
I have a issue with one PLC that takes much time to response to excel through DDE and on FactoryTalk Site Edition Local. I have already tried...
Replies
4
Views
2,129
Programming and saving a program while online is very slow, up to 20 minutes to save a program while online. I'm using a compaq nc8430, xp pro...
Replies
2
Views
2,531
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,553
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
Replies
8
Views
1,269
Back
Top Bottom