Hello,

I was wondering if a faulty or dead speed reference input in a Yaskawa SigmaII SGDH-02 servopack was possible ? I am supplying 5V to it and SigmaWin won't mention "Speed Reference Input" nor a value. I tried to reset, redo or exchange anything I thought of and my conclusion is :

  • servopack and motor jog fine using Sigmawin,
  • power, encoder, data cables are fine,
  • encoder outputs (same cable) from the servopack are fine.
Is there any chance it would be a replaceable 2-cents piece inside the servopack ? or did I miss the obvious "ignore speed reference input" parameter ? I certainly hope so.

Thank you very much,
Julien
 
Last edited:
Hello,

I was wondering if a faulty or dead speed reference input in a Yaskawa SigmaII SGDH-02 servopack was possible ? I am supplying 5V to it and SigmaWin won't mention "Speed Reference Input" nor a value. I tried to reset, redo or exchange anything I thought of and my conclusion is :

  • servopack and motor jog fine using Sigmawin,
  • power, encoder, data cables are fine,
  • encoder outputs (same cable) from the servopack are fine.
Is there any chance it would be a replaceable 2-cents piece inside the servopack ? or did I miss the obvious "ignore speed reference input" parameter ? I certainly hope so.

Thank you very much,
Julien

Welcome to the Forum!

I am not familiar with the Yaskawa Servos, I have only worked on their VFDs. However, I doubt that there is 2 Cent Component that will solve your problem.

Is this a new, or an existing installation?

Is the Speed Reference Unipolar or Bipolar? i.e. 0-10VDC or +/- 10VDC.

Stu.....
 
Hello,

and thank you for your answer.

Yaskawa SigmaII speed reference is +/-10V (one input and ground). The same connector is used for the speed reference, servo enable, limits, encoder outputs. I'm guessing the common ground isn't dead as the other inputs/outputs are fine.

This is a used servopack bought on eBay. I bought it ages ago but only tested it using "manual jog" mode before.

I own a few other Yaskawa (mainly 400W, no other 200W) who do work fine.

I forgot to mention all cables are shielded.

Thank you,
Julien
 
Hello,

and thank you for your answer.

Yaskawa SigmaII speed reference is +/-10V (one input and ground). The same connector is used for the speed reference, servo enable, limits, encoder outputs. I'm guessing the common ground isn't dead as the other inputs/outputs are fine.

This is a used servopack bought on eBay. I bought it ages ago but only tested it using "manual jog" mode before.

I own a few other Yaskawa (mainly 400W, no other 200W) who do work fine.

I forgot to mention all cables are shielded.

Thank you,
Julien

Julien:

I downloaded the Manual from Yaskawa, so hopefully it is the same one you are using.

I would go through all the Parameters in Section 9.7 of the Manual. Look for something weird in one of them. I see some that could shut you down if they are incorrect. For example, the Speed Reference Offset, and the Zero Clamp Parameter.

Stu....
 
Hello,

the drive was reset to "Speed control" multiple times.
Applying 5V to V-REF/SG, I could verify that it was entering the drive (to exclude cable/connector/noise issues) but SigmaWin wasn't reporting anything. I feared the "speed reference" circuit inside the drive was dead. So I switched to "torque control", used T-REF/SG and everything worked like a charm.
I would love to tell the drive "use Speed control but using T-REF input pin".
Have a nice day,
Julien
 
Hello,
the drive was reset to "Speed control" multiple times.
Applying 5V to V-REF/SG, I could verify that it was entering the drive (to exclude cable/connector/noise issues) but SigmaWin wasn't reporting anything. I feared the "speed reference" circuit inside the drive was dead. So I switched to "torque control", used T-REF/SG and everything worked like a charm.
I would love to tell the drive "use Speed control but using T-REF input pin".
Have a nice day,
Julien

It seems unlikely that the Servo Drive would support that, or they wouldn't bother with separate Inputs. It is certainly possible there is a failure in the Speed Input Components if you can't find a Parameter Settings issue. Have you had a look for anything obvious? Like burnt Components, or bad Solder Joints etc?

Stu....
 
Yes I did open it but didn't found anything obvious and couldn't track the circuit thru the PCB.

Thank you for the help, I guess it will be torque mode from now on.
 

Similar Topics

Dear forum members, By reffering to the blue labelled command on the attached file, Could you tell me what PLC register that is being limited by...
Replies
0
Views
74
What is the best way to extract the hour and minute from the register that comes from Yaskawa VFD. In studio 5000 I have a register saved as INT...
Replies
3
Views
161
Hi sir I has a equipment use Yaskawa GL60s PLC via P150 developer,we want to upgreat the system to New,but we have some problems For example: On...
Replies
0
Views
160
Hi Everybody, this may be one for you motion control guys. We have been tasked with interfacing some Yaskawa drives into a project where the...
Replies
0
Views
286
Hello, We have several Yaskawa GA800's installed in our plant. They are all controlled via Ethernet and they work fine. However, they all get...
Replies
0
Views
506
Back
Top Bottom