angi Member A Join Date Jan 2010 Location us Posts 361 Dec 7, 2012 #1 hi guys we need to use 1756_IF16, there are only 8 channels we could use when we configure it using Logix5000, how to configure the module for 16 channels? thanks
hi guys we need to use 1756_IF16, there are only 8 channels we could use when we configure it using Logix5000, how to configure the module for 16 channels? thanks
Craig Spinharney Member C Join Date Apr 2005 Posts 54 Dec 7, 2012 #2 angi said: hi guys we need to use 1756_IF16, there are only 8 channels we could use when we configure it using Logix5000, how to configure the module for 16 channels? thanks Click to expand... Make sure the "communications format" is set to one of the "single-ended" options. If you accepted the default ("Float Data- Differential Mode"), you'll have to delete the module and recreate it with the new settings.
angi said: hi guys we need to use 1756_IF16, there are only 8 channels we could use when we configure it using Logix5000, how to configure the module for 16 channels? thanks Click to expand... Make sure the "communications format" is set to one of the "single-ended" options. If you accepted the default ("Float Data- Differential Mode"), you'll have to delete the module and recreate it with the new settings.