hi guys
we need to use 1756_IF16, there are only 8 channels we could use when we configure it using Logix5000, how to configure the module for 16 channels?
thanks
hi guys
thanks
Make sure the "communications format" is set to one of the "single-ended" options.
If you accepted the default ("Float Data- Differential Mode"), you'll have to delete the module and recreate it with the new settings.
While troubleshooting an issue with an analog input card the other day, I removed the terminal block from the input card. Looking at the values in...
2,892
I have a 1756-IF16 analog card setup for “Float Data, Single Ended, No Alarm”. The device connected to the analog gives a 4-20ma signal which...
4,889
Good afternoon, I have a question with the Allen Bradley 1756-L83E. If I have multiple I/O cards (120VAC, 24VDC input output and analog cards)...
672
I would like a sanity check on an application i am working on. I have a proximity switch counting pulses with a Mark/space ratio of 1:1 on a...
1,878
I'm trying to find clarification from the Rockwell documents what it means to an L8x that controller connections are "not applicable" as in L7x...
1,578