Control Logix

mcannon

Member
Join Date
Feb 2013
Location
South Carolina
Posts
1
I need help....Please!!! I have a Control Logix processor and two plc5 remote chasis. I was having a issue with my outputs dropping out so I checked the box in the RIO card properties to give a major fault if I lost communication. I have cleared the fault but now I cant get my outputs back on. All of the output cards are dead(active light is not on). The remote cards on the plc5 racks have the active light flashing. From what I have read the scanner module is holding the adapter module in fault mode. I am not showing a fault anywhere, that I have seen anyway....Thanks
 
Well a major fault in the CLX needs to be cleared and the CLX put back into the run mode. Did you do this? Is the run light on in the CLX?
 
There are different selections for fault recovery on PLC5 Remote I/O adapters. Cycling the power on the remote chassis should clear a RIO fault, regardless of whether the local reset option via pushbutton closure is selected.
 

Similar Topics

I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
309
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
392
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
Replies
8
Views
810
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
Replies
1
Views
437
Hi all! I am hoping to find some help understanding the ABB VFD Connection to my Rockwell PLC. I have set up the VFD parameters based on...
Replies
4
Views
719
Back
Top Bottom