cqm1h not in run mode

msaadnegm

Member
Join Date
Feb 2013
Location
cairo
Posts
9
hello friends
i have a problem in plc omron cqm1h-cpu21
that when connect power to machine, the led of power supply of plc light and the led comm of plc blink
but nothing else, mean run and other leds don't light
one time, the plc work normal but after turn off and on the machine again, the problem get
 
Check to be sure that the PLC operating mode is set to RUN or MONITOR. You must be online to the PLC with CX Programmer to do this. The setting is under the PLC tab.
 
thanks mendonsy for your reply
i am trying to load the software, if you have direct link to cx-program i will be gratefull
but can the operating mode change itself ?
 
One thing about the CQM1 you should be aware of.
If the CQM1 detects a programming device connected to the peripheral port at power on, it will automatically switch to program mode.
 
One thing about the CQM1 you should be aware of.
If the CQM1 detects a programming device connected to the peripheral port at power on, it will automatically switch to program mode.
there is the operating sceen connected to cpu by RS232c
can it changing the operating mode?
if yes, how can i change to run mode for cpu?
does the dip switch in cpu affect the chsnging of operating mode?
what is the right position of dip switches for cpu?
i am sorry for much questions
 
See answers below:

there is the operating sceen connected to cpu by RS232c
can it changing the operating mode? No

if yes, how can i change to run mode for cpu?

does the dip switch in cpu affect the chsnging of operating mode?
No

what is the right position of dip switches for cpu?
See information below.

i am sorry for much questions

CQM1H_DipSwitch.jpg
 
i already installed a trial version cx-one 9.3 and also cx-programmer 6.1
and used a rs232c cable and make this connection:
pc (female) plc (male)
1 to 1
2 to 2
3 to 3
5 to 9
(4,6) (4,5)
(7,8)
and adjustbdip switch of cpu as:
1 off
2 off
3 on
4 on
5 on
6 off
7 on
8 off
the run cx-programmer and connect power to cpu after connecting thr rs232c cable and make direct online in cx-programmer
but give failed to connect to plc
i tryied to change dip switch many times but the same fail
what is the wrong thing i did?
thanks
 

Similar Topics

Hi Everyone, I have a customer that needs a CQM1H (CPU51) replaced. They purchased the processor new-old-stock from a source they found online...
Replies
3
Views
370
I have an Omron CQM1H-CPU21 and a NS8-TV00B-V1, I have followed the manufacturer's spec on how to set this up and all I got is the HMI is trying...
Replies
7
Views
908
Hello maybe someone can help me, I have omron CQM1H PLC with CLK21 (Controller link module) and SCB41 (Serial module connected with NMB CSD-891B...
Replies
1
Views
551
I need a CQM1H-CPU51 to talk to my Red lion Da30D i just need to read the status of some I/O and maybe read some data registers but I cannot...
Replies
7
Views
1,171
Hello, I need some help to convert PMCR instruction from Omron CQM1H that using CQM1H-SCB41 to CJ2M using CJ1W-SCU4, The problem is on the old...
Replies
1
Views
852
Back
Top Bottom