We are working on a project that includes the requirement for us to provide a 400A 480vac distribution panel with breakers to supply the 3-phase equipment and a transformer. We had planned to use an off the shelf panelboard with a 3R enclosure, but because the equipment is going in a washdown area all the panels have to be built using the Hoffman stainless steel slope top enclosures. I was wondering if any of you have done this type of thing using a bus and breakers from Square D and then just mounting this inside a Hoffman enclosure? Any suggestions otherwise?
 
We are working on a project that includes the requirement for us to provide a 400A 480vac distribution panel with breakers to supply the 3-phase equipment and a transformer. We had planned to use an off the shelf panelboard with a 3R enclosure, but because the equipment is going in a washdown area all the panels have to be built using the Hoffman stainless steel slope top enclosures. I was wondering if any of you have done this type of thing using a bus and breakers from Square D and then just mounting this inside a Hoffman enclosure? Any suggestions otherwise?

It's going to affect your UL rating (negatively, that is), but you can have a UL inspector come out and bless it (and get a new sticker in the process).

But the NEC is very clear about not allowing you to create your own system from various parts if there is an approved UL alternative.

When I worked for Kasa, we had a UL inspector come in and inspect every panel we built. At Schneider, the prototype was inspected and any subsequent panel built to that design had to follow the approved design exactly (I needed a pull-up resistor installed in the panel and even something as trivial as that was a no-no).

From a practical standpoint, I don't think there would be anything wrong with your approach. I've installed Square D "guts" in a FPE panel before. No problems, but not quite kosher either.
 
Actually I failed to mention we are a UL508 panel shop so I suppose we could build a panel with din rail mount breakers. However you then run into the issue of accessing the breakers without having to shut down the entire panel. I think this would be ok with our customer since all the equipment has local disconnects also.
 
Last edited:
What kind of wash down environment?
food, drugs, feed?
What wash down chemicals are being used?
it does make a difference as to the type of enclosure you use.

for food, its SS316 in several plants i know of.

regards,
james
 
If it has to be a Hoffman Watershed NSF-certified sanitary enclosure, then I would ask Hoffman/Pentair to make a custom modification and add a factory-installed UL-certified 400 Amp CB panel to the enclosure. Big $$$ cost, of course!
 
If it has to be a Hoffman Watershed NSF-certified sanitary enclosure, then I would ask Hoffman/Pentair to make a custom modification and add a factory-installed UL-certified 400 Amp CB panel to the enclosure. Big $$$ cost, of course!

Yea it is the Watershed. Don't really have time for a factory modification. We will probably build it ourselves. Hoffman actually sells a busbar system that we might consider. Going to see if AB has a similar product.
 
Actually I failed to mention we are a UL508 panel shop so...

Well, in that case, what does the UL guy say? I can't recall a UL listed piece of equipment that was done this way, but that is not to say that it would be illegal.

If you're talking about mounting the panelboard with the deadfront installed as if it were in its own enclosure (the ultimate extension of this thinking would be to mount the entire panel within the panel. Why not?), then where's the beef?
 
Well, in that case, what does the UL guy say? I can't recall a UL listed piece of equipment that was done this way, but that is not to say that it would be illegal.

If you're talking about mounting the panelboard with the deadfront installed as if it were in its own enclosure (the ultimate extension of this thinking would be to mount the entire panel within the panel. Why not?), then where's the beef?

I'm waiting to hear back from my UL rep about this. And your suggestion about mounting the entire I-Line panel inside the Hoffman is another option I have considered.
 

Similar Topics

Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
49
In our PLC, we've got a 24VDC (5 amp) power supply - it's a PULS cp5, which connects to a DIN rail. I need it to supply power to 8 x Druck...
Replies
2
Views
1,145
Does anyone know of a clever way to distribute 480 vac, three phase voltage for applications over 100 amps? I have a project where the customer...
Replies
18
Views
5,498
Hello Guys, I have a question thats not directly related to PLCs, but for those of you who work or have worked in contental Europe (anywhere...
Replies
4
Views
2,626
We have some issues with our main 1200A service that feeds part of our plant. It has ground fault interrupter relay which tripped four times since...
Replies
11
Views
3,808
Back
Top Bottom