factory talk studio me

RY_Guthrie

Member
Join Date
Nov 2011
Location
Las vegas, NV
Posts
263
I am trying to down load a application that I migrated from panel view to factory talk and i am getting cannot open project due to version incompatibility, I am not sure what this means , is it the version of factory talk me station? or ??
 
Typically I have seen this when the version of Factory Talk ME used to create the application is newer than the software on you laptop.
 
Or, if this is occurring when trying to run the newly created application on a Panelview Plus, it means that the firmware on the Panelview Plus is earlier than the application version.

That has happened to me a lot lately because a lot of Panelview Plus HMIs are still being shipped with 6.0 firmware but I was using FT View Studio 6.1.
 
Or, if this is occurring when trying to run the newly created application on a Panelview Plus, it means that the firmware on the Panelview Plus is earlier than the application version.

That has happened to me a lot lately because a lot of Panelview Plus HMIs are still being shipped with 6.0 firmware but I was using FT View Studio 6.1.

Ran into this too. In fact, I ordered TWO PVPlus 6 panels at the same time. One was running 6.1 firmware and the other was running 6.0
 

Similar Topics

I am trying to enable an external alarm via computer speakers for Factory Talk Network Distributed Edition. I am using Alarm and Events setup. I...
Replies
7
Views
172
I have some global objects, numeric display with associated data that pulls up a pop up screen. for the life of me i cannot figure out how it...
Replies
3
Views
238
Hello everybody. I was wondering if there is a way in FTVIEW Studio to close ) view after x min without interaction . My issue is the following...
Replies
2
Views
369
Is there a way to choose the base font in ME. Text in the Arial Unicode MS which is the default font on my FTVS doesnt show up properly on a...
Replies
1
Views
680
Hello all, looking for ideas on getting some basic training done, I need to practice on maintenance timers and bypass switches (with a Factory...
Replies
5
Views
1,318
Back
Top Bottom