MATT116
Member
Hardware
1756-L72
RSLogix 5000 V20
PIDE instruction
PowerFlex 400vfd
Grundfos submersible pump
The pump manufacture states that the pump should reach 30Hz in 3seconds and then operate at or above 30Hz. What would you guys consider good practice.
1) Limit the Hz using the CV Min of the PIDE instruction block and set it to 50% which with my scaling would be 12mA or 30Hz.
or
2) Limit the minimum Hz with the VFD using parameter P034[Minimum Freq] and keep the PIDE block CV Min at 0% so then 4mA would equal 30Hz.
Any pros or cons to either option?
Thanks
1756-L72
RSLogix 5000 V20
PIDE instruction
PowerFlex 400vfd
Grundfos submersible pump
The pump manufacture states that the pump should reach 30Hz in 3seconds and then operate at or above 30Hz. What would you guys consider good practice.
1) Limit the Hz using the CV Min of the PIDE instruction block and set it to 50% which with my scaling would be 12mA or 30Hz.
or
2) Limit the minimum Hz with the VFD using parameter P034[Minimum Freq] and keep the PIDE block CV Min at 0% so then 4mA would equal 30Hz.
Any pros or cons to either option?