The pump manufacture states that the pump should reach 30Hz in 3seconds and then operate at or above 30Hz. What would you guys consider good practice.
1) Limit the Hz using the CV Min of the PIDE instruction block and set it to 50% which with my scaling would be 12mA or 30Hz.
or
2) Limit the minimum Hz with the VFD using parameter P034[Minimum Freq] and keep the PIDE block CV Min at 0% so then 4mA would equal 30Hz.
Any pros or cons to either option?

Thanks
 
As a point of info, pump manufacturers may limit speed because below a minimum the pump isn't capable of enough head to overcome system resistance and so there would be no flow. That can result in vibration, overheating, and pump destruction. That minimum Hz is a function of system curve and pump curves and for the same pump may be different for different systems. A value like 30 Hz suggests to me the pump manufacturer is concerned about motor heating, which is also a valid concern.

I usually set the minimum Hz in the VFD parameters, as it keeps the amateurs from messing it up. To make life easy and make scaling consistent if the min Hz changes during commissioning or later on I keep 4 mA as 0 Hz and 20 mA as 60 Hz. Otherwise you keep having to re-think the speed/signal relationship during testing and servicing. Having 4 mA = 30 Hz and 12 mA = 45 Hz is going to confuse everyone and really has no benefit.
 
Thanks for the input guys
I agree the pump manufacture is concerned about heat and the back pressure on the thrust bearing or lack of. I think I will set Hz limit in the VFD
 
Agreed with Tom.. set in vfd. You can always limit an input to 30 and above. Keeping your relationship with speed control constant.
 
The only benefit to setting 30hz to equal 4ma is the increased resolution available when the analog to digital converter does its conversion. In a precision speed system, a/d resolution can be really important but, in this case, for a fan or pump, it is of no consequence at all. So, in this case, I'd agree with Tom that its best to do what's most understandable.
 

Similar Topics

we have 4 pump and we should know working time of them each time we start the system , a pump with minimum1 time should start if we need much...
Replies
21
Views
6,697
Hey there guys, I'm relatively new to PLC programming. I had a few basic classes in college but since then I have mainly been on the instrument...
Replies
3
Views
238
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
111
I've gotten to the learning curve where I can program a call for pump to come on at set point but I'm not sure how to turn the same pump off when...
Replies
1
Views
158
Hey Guys, I was looking for a little help on a school project. I was asked to program three pumps with two inputs, more and less. The project...
Replies
23
Views
2,591
Back
Top Bottom