Problem analog value S7 PLC

Jeroen Benoot

Member
Join Date
Oct 2006
Location
Oostkamp [BE]
Posts
42
Hello,

I am having difficulties setting up an analog measuring system with an S7 319F PLC.
The analog card is a 331-1KFO2-0AB0 13bit.
I have two of these cards in the configuration, both measure exactly the same; the feedback of a current supply, 2 analog values 0-5V.
At first the cards worked fine, but recently I see that the first card is working properly.
I measure the voltage on the connections (ex between 1 and 5) and that is a positive value, but when I check the value of the PEW it is negative?
The settings of both cards are exactly the same; +-5V

Does anyone have any experience with this?

Best regards,
Jeroen
 
At this point, the problem is gone: after recompiling the hardware and safety and downloading it again, the problem is gone;
I find this very strange, as I have not changed anything in the hardwareparameters.

But still thank you for the reply.
 
i noticed that in first post you mentioned 0-5V then -+5V.
Hello,

I am having difficulties setting up an analog measuring system with an S7 319F PLC.
The analog card is a 331-1KFO2-0AB0 13bit.
I have two of these cards in the configuration, both measure exactly the same; the feedback of a current supply, 2 analog values 0-5V.

(...)

The settings of both cards are exactly the same; +-5V
maybe you forgot to recompile and download the new system conf. settings
 
What I meant to say was that the settings of the input card are +-5V, (there is no 0-5V) and the value from the current supply is 0-5V, this should work like this.
 
I have experienced some similar, sometimes crazy values, on the same type of AI card.

In this case there was no ground/minus on terminal 10 & 11, do you have that?

Also the "negative" side of the channel must in many cases be grounded, but be careful with you potentials.

I can't remember how to do with +/- 5V or 0-5V, but read the manual. My guess will be yes.
 

Similar Topics

hello. i am using analog input module....2AI (6ES7 134-4GB52-0AB0) when i have applied the voltage like 7 or some time 9 volts...
Replies
6
Views
2,164
I am try to do this task: write FC1 that would read from analog input (analog input = tw). The output of the FC1 will be downloaded/read/recorded...
Replies
5
Views
2,934
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
Replies
1
Views
127
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
Replies
18
Views
1,515
Hi, Sorry for my bad english, I'm from Poland. I've decided to learn basic PLC programming as hobby and to maybe get a better job. I have...
Replies
2
Views
1,352
Back
Top Bottom