We have a storage silo here that is filled with flour. it is 10 feet in diameter, 18 feet tall and is cone shaped on the bottom with the feeder in the center of the bottom.
The fill line for the flour on top is slightly off center so top of the flour cone will be off center some what to.
We use 2 bindicators (220v) just to keep the silo full. The high level one is 1 foot from the top of the silo and we use another bindicator about 4 feet from the bottom.
About 3-4 times a year the high level bindicator fails. The shafts become clogged with flour and fail to shut the system off. It is not a pretty sight when the vent bags blow off and there is several thousand pounds of flour one the floor.
I am wondering what the recommendations are to replace these paddle type bindicators? I was thinking about ultrasonic or radar but I am not to sure which one will be able to "see" through the flour dust the best.
Also, this system is not set up on a plc system yet, but it is in the capitol request. Is there on sensor that has both discrete and analog outputs so it can be easily changed over when the plc is installed? The plc will be Allen Bradley.
Thanks for any suggestions or recommendation you may have.
The fill line for the flour on top is slightly off center so top of the flour cone will be off center some what to.
We use 2 bindicators (220v) just to keep the silo full. The high level one is 1 foot from the top of the silo and we use another bindicator about 4 feet from the bottom.
About 3-4 times a year the high level bindicator fails. The shafts become clogged with flour and fail to shut the system off. It is not a pretty sight when the vent bags blow off and there is several thousand pounds of flour one the floor.
I am wondering what the recommendations are to replace these paddle type bindicators? I was thinking about ultrasonic or radar but I am not to sure which one will be able to "see" through the flour dust the best.
Also, this system is not set up on a plc system yet, but it is in the capitol request. Is there on sensor that has both discrete and analog outputs so it can be easily changed over when the plc is installed? The plc will be Allen Bradley.
Thanks for any suggestions or recommendation you may have.