Hi to all,

We were having a discussion about wiring up a SLC500 power supply. I am sure that we have to use a separate neutral for each power supply circuit on each rack. If someone could let me know if this is correct or is it ok to use a common neutral to hook up several PLC racks? Thank you all for your help.
 
Assuming that all of the chassis are connected to the same transformer, there is no difference. Assuming that all of your control power transformers' neutrals are grounded (as they should be), there is no difference, although I'd still recommend connecting the neutral from the same transformer that sources your hot wire.

As a rule, I discourage daisy-chain connections of neutrals (or hot wires) in control panels or MCCs. This connection method can create problems when performing repairs, and can lead to overloaded circuits. I prefer to see each device have it's own wire connected to a central bus.
 
The main thing is not to overload your neutral, regardless of how many devices you connect to it. A neutral is a current-carrying conductor. It must have the same ratings factors applied as your hot wire. Whether you can add loads depends on the existing load + the proposed load. If your neutral is a #14 and you have 12 Amps on it (80% of the NEC allowed load for a 75-degree C rated #14 conductor), then you should not add additional loads.
 

Similar Topics

Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
264
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
Replies
1
Views
86
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
Replies
1
Views
969
What's everyone use for I/O drawings on new installs. I am trying AutoCad Electrical, but can't download it due to a MS Office application running...
Replies
11
Views
1,309
I've been tasked with adding a 3-wire pressure differential transmitter to a system and drawing up the wiring to an existing PLC board. The...
Replies
7
Views
781
Back
Top Bottom