Danfoss FC51

Akhund Yaseen

Member
Join Date
Nov 2013
Location
Hyderabad
Posts
2
Am using Danfoss VFD and Honeywell Pressure Transmitter, The Pressure Transmitter output is 4-20mA. And my application is like this...... when the 4mA or 5,6 mA source comes the motor RUNS at Max RPM and when the 17, 19 or 20 mA source comes the motor RPM goes LOW. Which parametre i used in Danfoss VFD.
VFD MODEL: DANFOSS FC 51.......

Its urgent Please reply ASAP.....
 
If you are trying to regulate pressure with VFD speed, then you should set up an external PID loop which will take care of this matter automatically.

If you are simply trying to regulate motor speed with the pressure transmitter, then you have to set up an inverted speed reference. There may be a specific parameter to do that or, more commonly, you set the max frequency parameter for the lowest desired frequency and the min. frequency parameter for the highest desired frequency.

Not being directly familiar with Dan Foss, I can't give you specific parameters to change.
 

Similar Topics

Having a small problem with a new danfoss micro VLT FC51 drive I was hoping someone on here could help with. my setup: my motor speed is...
Replies
4
Views
1,413
Hi all . Hope you are well . i need to connect to a drive ( Danfoss Microdrive FC51 ) through my laptop to get parameters backup . How can i...
Replies
7
Views
2,627
This is the first time I've had the pleasure of setting one of these up. It's a little 1.5kw, 3p 400v one running a centrifugal fan, 1.1kw motor...
Replies
6
Views
1,931
Hi Guys Took over a job where the customer has VLTmicro fc51 drives. Im installing a plc to control them so I would need a digital input from them...
Replies
3
Views
2,685
I need to control a FC51 Danfoss VFD with LS PLC. I need to start, stop & jog the drives. I have set all the parameters as per manual for Modbus...
Replies
3
Views
5,142
Back
Top Bottom