FC51 Danfoss VFD MODBUS
damiens
Mar 2009
Columbus
42
I need to control a FC51 Danfoss VFD with LS PLC. I need to start, stop & jog the drives.
I have set all the parameters as per manual for Modbus operation at 9600bps 8n1.
I am unable to start the drive I am sending the following frame to start the drive:
Address of Drive 2
Function 5
Coil 6
Data 1
Can someone help me, Danfoss service engineer has refused to help since I have not purchased the drive from their Official System House.
Hi Damiens!
I'm not in here as often as I would like, so I may be too late.
The Danfoss ModbusRTU requires Coils 2, 3, 4, 5, 6 and 10 to be high for the drive to run CW. Add Coil 15 to that mix and it will run CCW.
In the Danfoss world a stop command has higher priority than a start command (likely true in every reality), so you need to set all the Coils that in their "0" state have a stop meaning (2, 3, 4 and 5). Coil 10 "Data Valid" tells the drive if the data in the coils is to be acted upon, so this needs to be "1" for the drive to react on your command.
best regards
Michal_dk
Having a small problem with a new danfoss micro VLT FC51 drive I was hoping someone on here could help with. my setup: my motor speed is...
1,418
Hi all . Hope you are well . i need to connect to a drive ( Danfoss Microdrive FC51 ) through my laptop to get parameters backup . How can i...
2,633
This is the first time I've had the pleasure of setting one of these up. It's a little 1.5kw, 3p 400v one running a centrifugal fan, 1.1kw motor...
1,933
Hi Guys Took over a job where the customer has VLTmicro fc51 drives. Im installing a plc to control them so I would need a digital input from them...
2,686
Am using Danfoss VFD and Honeywell Pressure Transmitter, The Pressure Transmitter output is 4-20mA. And my application is like this...... when the...
2,968