DamianInRochester
Lifetime Supporting Member
Using an ET200S system with classic S7. I have three fail safe input modules of which the first six channels are direct wired estops (dual channel NC on both channels, single estop per channel).
Have them addressed in hardware as I100.0,1,2,3 and I106.0,1.
They are working fine in the safety program and are chained as inputs to a an FB215.
However, I have the same bits chained in some other code (that is called by OB1 once every scan) and it is indicating that I am getting a "flicker" on one or more of these channels. At first I though it was just a "monitoring/eyeglass" mode anomaly, but I put a counter off of it and sure enough it is flickering off for very brief time at random times that are around once a second.
Am I correct in believing that if the actual inputs were really flickering that it would have dropped out FB215? If so, what else could account for the discrepancy in the state of the safe input status between my normal code and my safety code?
Have them addressed in hardware as I100.0,1,2,3 and I106.0,1.
They are working fine in the safety program and are chained as inputs to a an FB215.
However, I have the same bits chained in some other code (that is called by OB1 once every scan) and it is indicating that I am getting a "flicker" on one or more of these channels. At first I though it was just a "monitoring/eyeglass" mode anomaly, but I put a counter off of it and sure enough it is flickering off for very brief time at random times that are around once a second.
Am I correct in believing that if the actual inputs were really flickering that it would have dropped out FB215? If so, what else could account for the discrepancy in the state of the safe input status between my normal code and my safety code?