CompactLogix 1768L43 with two 1768-ENBT

almk

Member
Join Date
Mar 2013
Location
Los Angeles
Posts
12
Hi. We have CompactLogix PLC 1768-L43 with two 1768-ENBT modules. One ENBT is configured for local network with VFD's and HMI, default IP is 192.168.100.1. Second ENBT is not used. Can we use second ENBT for client network connection with different IP like 192.100.100.1. Thanks for any info. Alex
 
Welcome to the Forum !

In terms of IP address and subnet, the 1768-ENBT modules are completely independent.

It is very common to have one configured for a private IP network running I/O and automation devices, and have another configured for an IP address on the business/enterprise network.
 
Ken,
Thanks a lot. So it is correct statement that two ENBT modules can have two totally different IP addresses, like one starts from 199.x.x.x and another 10.x.x.x? And both can be used to access PLC. Alex
 

Similar Topics

Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
95
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
98
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
Replies
3
Views
114
Hello all, and thank you in advance for any assistance you may be able to provide! This is my first post, so if I need to reformat or change...
Replies
8
Views
478
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
577
Back
Top Bottom