CompactLogix 1768L43 with two 1768-ENBT

almk

Member
Join Date
Mar 2013
Location
Los Angeles
Posts
12
Hi. We have CompactLogix PLC 1768-L43 with two 1768-ENBT modules. One ENBT is configured for local network with VFD's and HMI, default IP is 192.168.100.1. Second ENBT is not used. Can we use second ENBT for client network connection with different IP like 192.100.100.1. Thanks for any info. Alex
 
Welcome to the Forum !

In terms of IP address and subnet, the 1768-ENBT modules are completely independent.

It is very common to have one configured for a private IP network running I/O and automation devices, and have another configured for an IP address on the business/enterprise network.
 
Ken,
Thanks a lot. So it is correct statement that two ENBT modules can have two totally different IP addresses, like one starts from 199.x.x.x and another 10.x.x.x? And both can be used to access PLC. Alex
 

Similar Topics

Hi All, I'm just trying to understand the reason behind something I recently experienced. Background: The system contains 4 CompactLogix...
Replies
2
Views
130
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
282
Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
2
Views
171
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
125
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
Replies
3
Views
129
Back
Top Bottom