Citect V7.2 SP3 and Micrologix 1400

Terrep

Member
Join Date
Nov 2007
Location
Sydney
Posts
38
I'm having issues getting Citect to communicate with a Micrologix 1400.
I'm using the ABMLXEIP driver and followed the communications form in the help folder.
 
Post your settings for Board, Port and IO Device.

Have you checked the Citect kernel for diagnostics?

See attachment for a working ML1100 setup which is the same needed for ML1400.

CitectMLSetup.jpg
 
Hard to tell from the pics but from what I can see you are missing a space between the IP address and the -P0 -T in the Special Opt. for the Ports form.

It should be -I192.100.50.100 -P0 -T

You need to go to the IO devices page in the Kernel for diagnostics on the IO Device.
 
I've put the spaces in and restarted. I've opened up the I/O Device window in the kernel and it had the following message ' No unit statistics available as this is not an IO Server'
 
Pretty sure this happens when the network address you entered in the Citect config doesn't match the actual IP address of the machine you're trying to set up.
 
Are you sure your computers IP is set to 192.100.50.130 which is the IP you set in the Citect Network Address form?

How many network interfaces do you have?

If you have more than one NIC, then it could be a problem.

Try setting this parameter in Citect.INI to force the role to server/display.

[Client]ComputerRole=0
 
I was able to select the server option. And there is a server in the kernel I/O device. But it still isn't communicating with the PLC.

project editor.jpg citect kernel.jpg Internet protocol properties.jpg
 

Similar Topics

Dear all, Can I ask something ? I can't create any animation movement at equiptment design in my HMI can you tell me how to create this use a...
Replies
0
Views
1,475
I have problem with connecting citect with S7300 CP343-1 through PSDIRECT , i follow procedures of manual but i one of installation steps need to...
Replies
0
Views
1,741
Hello, I have a running project on Citect v5.42 and simatic net v6.4 I have created a new spare PC and loaded all software like Citect, station...
Replies
0
Views
68
Hello everyone, In a factory where we installed Citect 7.20 the computer began to show the first signs of end of life. They never considered...
Replies
0
Views
73
I have a running backup of Citect and plc and I want to make a spare PC station so I have installed the win XP and somatic net v6.0 and import the...
Replies
3
Views
121
Back
Top Bottom