Hi guys,
I'm new to studio 5000 & factory talk view,
I believe its simple but I cannot figure the answer. I want to use a TAG value to change my display graphic (page) on the panel view.
 
Welcome to the Forum !

Each Display has a Display Number that's set in the Display Settings (right-click, select Display Settings). By default it is Zero, so you have to manually change it for every Display.

That Display Number can be used with the PLC in two ways:

1. The PanelView writes the Display Number to a Tag in the PLC so that the PLC knows what screen you're on.

2. The PanelView reads a Tag from the PLC and navigates to that Display Number when the number is nonzero.


Both of these features are configured in the Global Connections section of the Project Organizer.

"Replace Display Number" is the Tag to which the PanelView writes the currently open Display number.

"Remote Display Number" is the tag that the PanelView reads from the PLC in order to change displays when the value is nonzero.
 

Similar Topics

I'm a beginner to PLC and Hmi programming. any one please help how to connect HMI to pc. HMI has a printer **** enabled by default, It does not...
Replies
5
Views
432
Hello, I've recently tried to upgrade my PLC controller from a L72 to L84ES and everything seemed to work, all buttons and screens as far...
Replies
9
Views
2,652
I imported the pva into Factory Talk View Studio and it gave me some errors. Alarm message Ack option not supported. Blinking color images are...
Replies
3
Views
1,795
I'm trying to set the date and time on a Panelview 600 plus 2711P-T6M20D8 SER A. I looked for a white square to pop up in the lower left...
Replies
6
Views
1,806
Hello forum, Simple question from a newbie. We have a PV600 showing all nodes in error. The Link coupler power LED is not illuminated and a...
Replies
5
Views
2,027
Back
Top Bottom