Connect the load cell to any weight transmitter. The transmitters have analog outputs (4-20ma or 0-10V) that you can connect to the analog input of any PLC. you can also have transmitters with Profinet, Devicenet, Profibus etc.
This is an example of a weight transmitter : JOLLYTLB from Laumas Elettronica.
As nonuke said, you need a signal condition to convert the load cell signal to a 0-10V or 4-20mA signal. Also, if memory serves me correct, the micrologix1200 does not have built in analog inputs. You will also need an analog input module for your PLC.
i have used beam, s-beam, tension, compression, button head,
summation load cells.
i agree with the others, but you must also be aware of sudden inpact or shock in regards to the load cell. load cell shock can be as much as 6-10 times its capacity.
you must also be careful not to place a load on the loadcell when you put it in place and tighten it in place.